- Location
- Bremerton, Washington
- Occupation
- Master Electrician
OK we know the code allows more wires in a conduit than is practical. 15 THHW's in a 3/4" RMC, which carry a 50% adjustment factor for fill.
With 12, that goes from 30 amps to 15. Seems like the reasonable fill is 7-9 conductors at 70%, that puts you at 21 amps.
I did find a 3/4" RMC with 23 12 THHWs in it once.
With 12, that goes from 30 amps to 15. Seems like the reasonable fill is 7-9 conductors at 70%, that puts you at 21 amps.
I did find a 3/4" RMC with 23 12 THHWs in it once.