I'm trying to understand why balancing a load one way is better than the other? Here's the exam question.
Balance a 120/240v delta 3 phase panelboard in kva for the following loads: One 18 kva 3 phase, two 5 kva 1 phase 240v, and three 2 kva 120v.
ex 1:
a= 6.0 kva + 2.5 kva + 2 kva + 2 kva = 12.5 kva
b= 6.0 kva + 2.5 kva + 2.5 kva = 11.0 kva
c= 6.0 kva + 2.5 kva + 2.0 kva = 10.5 kva
ex 2:
a= 6.0 kva + 2.5 kva + 2.5 kva = 11.0 kva
b= 6.0 kva + 2.5 kva + 2.5 kva = 11.0 kva
c= 6.0 kva + 2.0 kva + 2.0 kva + 2.0 kva = 12 kva
ex 3:
a= 6.0 kva + 2.5 kva + 2.5 kva + 2.0 kva = 13.0 kva
b= 6.0 kva + 2.5 kva + 2.0 kva = 10.5 kva
c= 6.0 kva + 2.5 kva + 2.0 kva = 10.5 kva
ex 1 = the answer given.
ex 2 = my 1st answer. [neutral not balanced]
ex 3 = my 2nd answer. [neutral balanced]
If my thinkings right, I need to know the rules for BALANCING ???