Going over this practice question for my code test. Thought I was right to base it on the 60 degree column because the information wasn’t given if terminals were rated higher, and it was less than 100 amps...
A trade size 1 1/4 Conduit contains 3, 3 phase motor circuits and an equipment grounding conductor. The motors run at the same time and the conductors are number 8THHN copper. What is the allowable ampacity of these conductors?
From nec table 310.16, the allowable ampacity of a number 8THHN copper conductor is 55 A.
The 55 ampere rating is based on not more than three current caring conductors in the raceway and an ambient temperature of 30°C
Because a different ambient temperature is not stated, no correction for ambient temperature is required, the percentages given in NEC table 310.15(c)(1) to the ampacity listed in the table or applied
In this case it is 70% based on the nine current caring conductors.
Note: NEC section 310.15 F provides that the equipment grounding conductor is not counted when applying the provisions of sections 310.15(c)(1).
55×.70 equals 38.5 A
A trade size 1 1/4 Conduit contains 3, 3 phase motor circuits and an equipment grounding conductor. The motors run at the same time and the conductors are number 8THHN copper. What is the allowable ampacity of these conductors?
From nec table 310.16, the allowable ampacity of a number 8THHN copper conductor is 55 A.
The 55 ampere rating is based on not more than three current caring conductors in the raceway and an ambient temperature of 30°C
Because a different ambient temperature is not stated, no correction for ambient temperature is required, the percentages given in NEC table 310.15(c)(1) to the ampacity listed in the table or applied
In this case it is 70% based on the nine current caring conductors.
Note: NEC section 310.15 F provides that the equipment grounding conductor is not counted when applying the provisions of sections 310.15(c)(1).
55×.70 equals 38.5 A