Recently took a pre employment test. Had a question on one of the calculations. Question asked find branch circuit load for 1 counter mounted 6kw range and 2 wall mount ovens at 4 kw a piece. As per note 4 on 220.55 you can count them as one which is 14kw. Then in note 1 you increase column c 5 % for each kW over 12. So I added 10% to the 8 and multiplied 18% x the 14kw and came up with 2.52 then subtracted that factor from the 14kw and put 11.48kw as the branch circuit load. Am I right with this answer? Any help would be appreciated.