Are you saying that a truck will drive into this structure and will be washed inside the structure? That would make the entire interior a wet location, and anything electrical (lights, receptacles, wash pump motors, etc.) would have to be listed for that environment. Reference 110.11.
In terms of power to the building, you are in 225 (outside feeders) and not 230 (services).
Since this is not a dwelling unit, there are no specific requirements for installing receptacles. Also, Table 220.12 doesn't list your type of structure, so you are on your own for including sufficient capacity for lighting loads.