In an electrical room, protected by a Preaction sprinkler system, there is a sprinkler pipe that crosses over the top of some of the gear. The pipe is located more that 6ft above the top of the equipment. My question, since the pipe contains air unless both a sprinkler head activates & smoke detector activates, would this pipe require drip pan? Or would the Preaction system be considered the leak protection as required by 110.26(F)(1)(b)?
Since I caught this in a shop drawing review, I will make the FP contractor relocated the pipe as a matter of good practice. But I?m curious what other think.