but I cannot think of any areas where I really like the 3500K.
The Government uses a huge amount of lamps and 835 is a fairly common specification. RFQs come in. You use materials that meet materials that all of their shalls or get left out as non-responsive or get called out by competing bidders to get you off the list.
The purchasing specification writers don't necessarily know what they're doing and are sometimes influenced by manufacturers sales reps. You see the lamp manufacturers playing games with 1-2 CRI points, or some insignificant just so they don't get left out of the game.
Here's an obvious Philips exclusivity favored requirements from a public purchasing specification of a Tennessee institution. :lol:
A. General: Provide lamps to match the requirements of the luminaire and ballast in
which they are installed. Subject to compliance with these specifications,
provide fluorescent lamp from one of the following manufacturers:
General Electric
Phillips
Sylvania
B. Standard T8 fluorescent lamps shall be medium bi-pin lamps suitable for instant
start or rapid start ballasts. Lamps shall be in lengths as required for the fixture
installation and shall be 3500 degree Kelvin color temperature, 86 color rendering
index minimum, 20,000 hour rated average life. Mean rating for a 4-foot,
standard output lamp shall be 2800 lumens. All T8 style fluorescent lamps shall
be low Mercury and Toxicity Characteristic Leaching Procedure (TCLP)
compliant, and
shall have green endcaps to demonstrate compliance.
You can't not use Philips and meet both requirements. Brochures often have "architectural specifications" written in that manner in a way that favors them in a hope that someone at purchasing will just copy and paste and change out a few words.
Since Philips green end caps are Philips' trademark, that spec writer effectively locked their option to Philips exclusive without blatantly/intentionally violating sole supplier rule.