I got red tagged for not using bonding bushings or grounding lock nuts on the 8" nipples that stubbed up into the bottom of my first distribution panel from the 12470 to 480 pad mount transformer . The inspector called it a service panel. I call it a SDS and said 250.97 exception #2 was all that was needed with plastic bushings.He said it was like a service and had to follow the rule for service raceways.The transformer is fed from a feeder breaker ( privately owned) in the switch yard down stream from the primary service conductors.This was all on top of him calling my distribution panel from my gen set (non SDS) a service panel and wanted a bonding jumper installed. No ifs ands or buts.So he gave me the red tag.