All of the concrete on this project is sealed from moisture intrusion and the AHJ and EOR have both deemed that the rebar will not be a proper ufer ground. The EOR has stipulated driving a rod in lieu of using the rebar but he has not stiplulated bonding the rebar to the rod. The detail does require bonding to the cold water pipe in the building within 5' of point of entry.
We want to bond the rebar, the EOR has stated this is not necessary. We contend that all potential current carrying items should be effectively bonded to ground, including the rebar.
Your opinions?
We want to bond the rebar, the EOR has stated this is not necessary. We contend that all potential current carrying items should be effectively bonded to ground, including the rebar.
Your opinions?