Pressure transducer grounding

Learn the NEC with Mike Holt now!

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
I have seen some instrument techs on PT cut the grounding wire off of the seal tight (bonding jumper that is spec from gas company to wrap the sealtight with ) after the transition from RMC. But there is still the EGC inside the raceway that connects to the internal of the PT.
 

4-20mA

an analog man in a digital world
Location
Charleston SC
Occupation
Instrumentation & Electrical
Might have been trying to eliminate some noise or interference like on some flowmeters. Possibly? Some of the bonding is overkill I think sometimes.
 

4-20mA

an analog man in a digital world
Location
Charleston SC
Occupation
Instrumentation & Electrical
Yea, I dont agree with the method, but lots of pressure transmitters have a place for a bonding jumper to land on a screw on the outside of a transmitter. So noise isn't the most prevalent, but they want them bonded for some reason, it seems.

All 3 of these types do, right there on the right-hand side of the transmitter head.

Hell, around here, I'll try anything to keep a good steady zero or reading in general. Including bonding!
5ecb7e4f0fddd0175708a5ea3948201e.jpg
 