1. At a duct burner purged enclosure in a Power Plant the exit L fittings should be explosion proof.
I do not agree w/this statement, because as per NEC-2005
501.15B2(Exception 3): "Conduit systems from an enclosure or room that is unclassified as a result of pressurization into Cl1 Div2 location shall NOT require a seal at the boundary"
Also the enclosure is Type Z which is satisfying the requirements in NFPA-496 art 4.8.3 for
alarms and 4.8.1 for detection of low pressure etc.Am I right?
2. The enclosure is NEMA4 and the pressure system is UL...Does this combination make the hole system (Enclosure and system) complying with NEC-110.3 regarding use as intended? I cant imagine UL-ing the pressure system without an enclosure.