So I will be installing (3) Solaredge 7600 inverters (32 amp continuous output). All of their AC outputs will land in a combiner panel before heading to the main panel. So (3) 40 amp breakers in the combiner panel.
So.......32 amps+32+ 32= 96 amps. Muliplied by 1.25 and get 120 amps. This is my full inverter output adjusted for continuous load.
Now to size wire. Looks like if I use THWN-2 or THHN I can go safely with #2 conductors (good to 130 amps) with a 125 amp breaker in the main panel.
Does this look right?
Thanks