godsquadgeek
 - Western, United States
 - industrial electrician for food processing facility
Is it UL Listed?
If so it is probably safe. If not, it may not be. But I do not see anything particularly wrong with it.
What is it that is bothering you?
If this is meant to be US/NEMA receptacle (and you have not flipped the picture since the text reads properly) it looks like the wide slot is on the wrong side in the pattern.
It's a 6-50r to 5-15p adapter. The pinouts are correct for those types. Appears to be a molded/factory cord and not a photoshop. No idea why you'd need a cord like this... maybe some welders on a low enough setting could get by on a 15A circuit?
A lot of adapters are made up for connecting RV or trailer shore cables to unofficial power sources. This might be one of those.
As long as the receptacle it plugs into is protected by a properly sized breaker it should be safe. The user simply has to be careful to keep their power drain down to avoid trips.
Those are usually a variety of 120/240 connector types though.
it was an adapter bought for a small mig welder, hand held.
good follow up, tho that begs the question: if the mig welder was capable of running on a 15A circuit, then why did it come with the 6-50 from the factory??
I think many welders are now smarter than the old ones.
I had to run a temp feeder for a welder on a job site and asked what it needed and I was told 200-250 volts, 30 to 60 amps, single or three phase. :huh:
I walked away laughing to myself, '220, 221, whatever it takes'
Well when I looked at the welder that was the deal, it had a label on it explaining you could connect it single or three phase and it would self adjust to it.
I have a dozen or so screwdrivers with burned tips to attest to that...You can even weld off a 12VDC car battery.