A friend is looking at a future upgrade to 400A service. There's a 180 ft run from the existing PoCo xfmr to the meter.
He's had a hard time with the PoCo's responses to his queries; after 2+ months delay, he was told his existing 4/0 was OK for a 320A upgrade.
But he breached the wall and actually talked to an engineer there who was aghast at that. So he's worried he should be burying duct for ~350MCM as part of another project.
I'm curious how a run of three 350MCM compares costwise to the same length of HV coaxial cable.
Yes, there are other factors such as the xfmr cost, but I gotta start somewhere.