Can you run the 480v Primary to transformer and the 120/208 secondary leaving transformer in the same conduit.
Can you run the 480v Primary to transformer and the 120/208 secondary leaving transformer in the same conduit.
As mentioned by Bob and Bob derating will kill you unless you can limit the single conduit to 24" or less.
Can you run the 480v Primary to transformer and the 120/208 secondary leaving transformer in the same conduit.
You do not run the neutral with the primary feeder conductors, so that is not an issue....
You do need to distinctly mark the neutral conductors of both systems. The practice is white for 120/208, and gray for 277/480.
...