Hello,
the previous designer specified 50 for primary and 100 for secondary. i came up with 150 for primary and 175 for secondary.
here's how i got there from Table 450.3(B) of the 2014 NEC:
Primary – 480 V single phase
Full load amps: 30000/480=62.5
Protection can’t be more than 62.5*2.5=156.25
Next size down – 150 A CB
Secondary – 120/240 V single phase
Full load amps: 30000/240=125
Protection can go to next standard size up from 125*1.25=156.25
Use – 175 A CB
why would one go lower? is there some benefit or rule i'm not aware of? thanks in advance.