Primary disconnect for transformers

Status
Not open for further replies.
NEC 450.14 allows for transformer primary disconnects to be located remotely if they are "lockable". Is permanent add-on locking hardware for individual circuit breakers, installed by the (electrical) equipment manufacturer in an MDP, acceptable to meet code requirements?
Thank you.
 
2014 NEC

450.14 Disconnecting Means. Transformers, other than Class
2 or Class 3 transformers, shall have a disconnecting means
located either in sight of the transformer or in a remote location.
Where located in a remote location, the disconnecting
means shall be lockable in accordance with 110.25, and its
location shall be field marked on the transformer.

If it complies with 110.25.
 
NEC 450.14 allows for transformer primary disconnects to be located remotely if they are "lockable". Is permanent add-on locking hardware for individual circuit breakers, installed by the (electrical) equipment manufacturer in an MDP, acceptable to meet code requirements?
Thank you.

IMO yes.
 