primary disconnect required in sight for MV transformer?

Status
Not open for further replies.

malachi constant

Senior Member
Location
Minneapolis
We have an existing installation where the utility brings 13.8kV into the building. From there we have a lineup of MV switches that distribute out to transformer vaults within the facility (all one building, not a campus). These vaults contain (3) 1P cans that we are replacing with dry type 13.8k:208V equipment. Do these need to have additional primary protection within the vault (i.e. in sight of the transformer), or does the primary switch back at the service suffice? A question from a vendor has got me looking to verify, but I haven't found anything requiring it in NEC 240 or 450. Thanks!
 
We have an existing installation where the utility brings 13.8kV into the building. From there we have a lineup of MV switches that distribute out to transformer vaults within the facility (all one building, not a campus). These vaults contain (3) 1P cans that we are replacing with dry type 13.8k:208V equipment. Do these need to have additional primary protection within the vault (i.e. in sight of the transformer), or does the primary switch back at the service suffice? A question from a vendor has got me looking to verify, but I haven't found anything requiring it in NEC 240 or 450. Thanks!

See 450.3(A) for transformer protection requirements and 450.14 for disconnecting means.
 
450.3(A) transformers over 1000V, OCPD shall be per table 450.3(A).
-->Table 450.3(A), max primary protection over 1000V, fuse rating = 300%. Note 1 is regarding if not a standard size than round up.
I don't see anything there that requires this be in the same room.

450.14 disconnecting mean. Transformers shall have a disconnecting means located either in site of the transformer or in a remote location. When in a remote location the disconnecting means shall be lockable in accordance with 110.25, and its location shall be field marked on the transformer.

So I think that answers my question - we are good here. I may be able to make it fit and will make sure the Owner is in the loop on making the decision. Seems like a reasonable enough safety precaution.
 