Obviously the fuses should be sized to handle the inrush, but why would only one phase blow during the startup of a 3-phase transformer?
Obviously the fuses should be sized to handle the inrush, but why would only one phase blow during the startup of a 3-phase transformer?
And once one fuse blows, only possible current left is between the other two phases which have different time for zero crossing point.Inrush is usually higher on one phase depending on when the switching occurred relative to the voltage waveform. Switching at a zero crossing will always give you the worst case inrush.
Sent from my iPhone using Tapatalk
There are different types of fuses depending on the application,,,,,,,,,,,,,,Obviously the fuses should be sized to handle the inrush, but why would only one phase blow during the startup of a 3-phase transformer?
210505-1710 EDT
Xtptcrewx:
Why?
See my scope plots at:
See P6 and P7.
Whether the core is driven more into saturation, or not, at application of voltage, is a function of the direction of residual flux in the core at the turn on time, and the direction in change of flux as a result of the applied volt time integral.
.
210512-2252 EDT
Xptpcrewx:
The linear transient current (no core saturation) resulting from applying voltage to an unloaded transformer at a voltage zero crossing is relatively small compared to the transient current from the core being driven into saturation. The transient current plot that I made and referenced is the real problem in most cases of tripping an over-current device on the primary side.
.
So is this a true 3-phase transformer with a delta or wye primary, or is it a V-V (open delta) or T-T connection of two single phase transformers (sometimes T-T's are in a single housing, not sure about V-V's) ?Obviously the fuses should be sized to handle the inrush, but why would only one phase blow during the startup of a 3-phase transformer?
Are those on wire instead of tape? Ampex had their first production audio tape recorder in 1948.210517-1457 EDT
... I still have magnetic recordings from the early days that are in good condition, meaning late 1940s.
I usually refer to published maximum practical inrush current factors of transformers. On one Eaton data, I have found out that the bigger the kVA, the smaller the maximum practical inrush current factor! That only shows that the bulkier cores will give you a better and manageable inrush than a transformer of the same capacity with a higher designed operating flux (smaller core)! Hope this helps on others' decision-making!
winnie:
What I am focused on is a controlled experiment on transformer inrush current. This really has nothing to do with steady state current. My experiment has to do with the initial flux state of the transformer core at the time that voltage is applied, applied source voltage (assumed very low impedance relative to the transformer load that will develop upon application of voltage), voltage is a sine wave of known voltage and frequency, and that voltage is turned on at a zero crossing. Two zero crossing phasings are possible. One increases the flux and the other decreases it. I pick the increasing one to force the core further into saturation. Note turning on voltage at a voltage zero crossing produces the greatest amount of flux change.
The linear transient current (no core saturation) resulting from applying voltage to an unloaded transformer at a voltage zero crossing is relatively small compared to the transient current from the core being driven into saturation. The transient current plot that I made and referenced is the real problem in most cases of tripping an over-current device on the primary side.