Table 450-3(b) indicates 250% MAX for primary protection, when both primary and secondary will be provided.
On the other hand, if the load on the secondary is fixed and will be low, how close has anyone set the primary OCPD relative to the FLA.
I don't want to go below 125% of primary FLA to avoid nusiance tripping during in-rush, but I am being asked if there is a code violation to go to 95% to save some $$$.
I realize on large transformers the inrush could be as high as 6x FLA, but is the inrush so severe on small transformers (<75kVA)?
Code references?
On the other hand, if the load on the secondary is fixed and will be low, how close has anyone set the primary OCPD relative to the FLA.
I don't want to go below 125% of primary FLA to avoid nusiance tripping during in-rush, but I am being asked if there is a code violation to go to 95% to save some $$$.
I realize on large transformers the inrush could be as high as 6x FLA, but is the inrush so severe on small transformers (<75kVA)?
Code references?