For a transformer less than 600V, is it permissable to size the overcurrent protection on the primary at LESS THAN the nameplate primary full-load current rating? Is it permissable to size the primary OCPD based instead on the secondary load current? For example, a 75kVA transformer serving a 45kVA load - can the primary OCPD be sized at 54A (FLA at 45kVA) x 1.25 or should it be 90A (FLA at 75kVA) x 1.25, or is even even less acceptable? If it is permissable to undersize the primary OCPD, where is it stated (or is it acceptable by not being addressed?)? If not acceptable, where is that stated in the NEC?