4 #4electric Member Location watertown,ny,jefferson Feb 3, 2013 #1 a trans. has a rated pri. current of 90 amperes at 480v. what is the maximum rateing permitted for primary overcurrent protection if secondary overcurrent protection is ommitted
George Stolz Moderator Staff member Location Windsor, CO NEC: 2023 Occupation Hospital Master Electrician Feb 3, 2013 #2 This looks like a homework question. We will not do your homework for you, but we will assist you in understanding the NEC. Where have you looked? What are the key words in the question?
4 #4electric Member Location watertown,ny,jefferson Feb 4, 2013 #3 from table 450.3(b) current over 9 amps. 90x125%=112.5. no such breaker size, so next higher one is 125amp.from 240.6.
david luchini Moderator Staff member Location Connecticut Occupation Engineer Feb 4, 2013 #4 #4electric said: from table 450.3(b) current over 9 amps. 90x125%=112.5. no such breaker size, so next higher one is 125amp.from 240.6. Click to expand... That is correct.