I have a 480/277Y, 3 phase, 4 wire panel and I'm looking at installing a 1kva 480v - 120v step-down transformer to feed a specific piece of equipment. I come up with 1.2 amps for the primary current. Table 450.3(B) sets my primary only protection at 300% and I don't see anything that says if this does not correspond with a standard breaker rating, I can use the next size breaker. I was hoping to use a 2-pole 15a or 20a breaker to feed the transformer but it doesn't look like I can. Don't have a lot of experience with transformers, so any help would be appreciated. Thank you.