Current situation: a 3 phase, 75KVA 480 - 208/120 transformer fed from 480V bus duct with 100amp fuses on primary with #2 THHN wire and the secondary has 2 taps made at the transformer, (1) tap #1/0 THHN has 60' feet of wire then terminating on a 150 amp breaker at a machine, the other tap is also 60' #1/0 THHN terminating on another 150 amp breaker. Does this meet the NEC for "transformer primary protection only" with a maximum of 100' tap? ref: Table 450.3(B) , 240.92 (C), and does 240.4(F) apply? NOTE : The conductors are protected meeting 240.92(C)(3). Can 90 degree table be used for calculating 240.92(C)(1)(1) although the termination are 75 degree. One last comment can 460V be used in place of 480 for the calculation in 240.92(C)(1)(1)?
Thank You
Tom