I’m looking at a 13.2 kV primary switchgear with with three radial feeds, each with 3 #1/0 AWG aluminum conductors. These are rated for 155A. Each radial feed has Cutler Hammer RBA 400 100E fuses. The feeds power a series of distribution xfmrs on a campus. I came to realize that E fuses melt at 2 to 2.4X their rating after 300 seconds which has left me perplexed. Is this feeder protected? Is there a code or standard that permits a fuse to exceed the rating of the feeder? I’m worried about one of the feeds drawing 175 Amps with no forseable way to clear an overload. Any input would be appreciated.