I know when you have a utilization voltage service transformer, you bond the neutral and ground buses at the service entrance equipment and from that point you are running 3P, 4W, plus an equipment ground through the whole system.
The question I have is with primary switchgear used to distribute power through a campus. Say you have a grounded wye connected 13.2 kV substation with three phases and a neutral that feeds a 3P, 3W (Three phases and one ground bus, not sure if 3P, 3W is a correct classification) primary switchgear of the same voltage. I'm noticing that the gear does not have a both a neutral and a ground bus, but a single ground bus. Should the neutral from the substation be tied directly to the singe ground bus, as well as the switchgear grounding electrode system? I'm confused because typically I'm used to seeing a neutral and a ground bus in 480V gear. It seems to be when talking about "neutral" and "ground" at a primary switchgear, the terms are interchangeable and both the neutral and the electrode system are tied to the same bus.
Second question. If I don't run the neutral from the substation to the ground bus in the primary gear, and just establish an electrode at the gear, is the system still grounded because the substation transformer upstream is grounded?
Thanks!
The question I have is with primary switchgear used to distribute power through a campus. Say you have a grounded wye connected 13.2 kV substation with three phases and a neutral that feeds a 3P, 3W (Three phases and one ground bus, not sure if 3P, 3W is a correct classification) primary switchgear of the same voltage. I'm noticing that the gear does not have a both a neutral and a ground bus, but a single ground bus. Should the neutral from the substation be tied directly to the singe ground bus, as well as the switchgear grounding electrode system? I'm confused because typically I'm used to seeing a neutral and a ground bus in 480V gear. It seems to be when talking about "neutral" and "ground" at a primary switchgear, the terms are interchangeable and both the neutral and the electrode system are tied to the same bus.
Second question. If I don't run the neutral from the substation to the ground bus in the primary gear, and just establish an electrode at the gear, is the system still grounded because the substation transformer upstream is grounded?
Thanks!