The primary voltage is 4160 v to a transformer the secondary voltage is 208/120 v why do they use 4160 volts ? ( mathematical )
I believe that the standard voltages were chosen because they were determined to be the most efficient voltages for power distribution.
The higher the voltage, the lower the current for the same amount of power.
DC is more efficient than AC.
I think like a lot of other things, voltages were just chosen because they were chosen. There does not appear to be any reason to a lot of it to me. For the most part, it probably does not make much difference. The difference between selecting 4160 V and (just as examples) either 3500 V or 4500 V, probably just does not matter.
Why did some places select 60 Hz and others 50 Hz. There are even a very few places using 25 Hz IIRC.
Not sure how those two fit together....4160 is a phase to phase voltage and 7200 is a phase to ground voltage from a 12470 volt 3 phase wye system.T...I won't get into the detailed math behind transformers but to prove my point, multiply 4160 by the square root of 3... you get 7200V. Which is another standard distribution voltage. ....
Not sure how those two fit together....4160 is a phase to phase voltage and 7200 is a phase to ground voltage from a 12470 volt 3 phase wye system.
I believe that one of the earlier systems was 2400 volts, and often single phase transformers were used connected in delta....you can reconnect those same transformers in wye and feed them with 4160.
Did not know that 7200 is a phase to phase voltage....the only places I have seen it was as phase to ground. Thanks.both 7200/3 and 12470/3 ph-ph are common in mining
as was said they kept increasing voltages as technology advanced and demand increased
2400 x sqrt 3 = 4160
4160 x sqrt 3 = 7200
7200 is 12470
And so on
there are some gaps but for some reason engineers like sqrt 3 lol
Did not know that 7200 is a phase to phase voltage....the only places I have seen it was as phase to ground. Thanks.
both 7200/3 and 12470/3 ph-ph are common in mining
as was said they kept increasing voltages as technology advanced and demand increased
2400 x sqrt 3 = 4160
4160 x sqrt 3 = 7200
7200 is 12470
And so on
there are some gaps but for some reason engineers like sqrt 3 lol
Here is a paper I stumbled across where the first few pages discuss the evolution of distribution voltages:
http://www.cooperindustries.com/con...urces/library/201_1phTransformers/R201902.PDF
Here is a paper I stumbled across where the first few pages discuss the evolution of distribution voltages:
http://www.cooperindustries.com/con...urces/library/201_1phTransformers/R201902.PDF
4160 volts has been a standard medium voltage rating for distribution systems for many decades. I don't often see it along city streets. But I do see it in large industrial complexes and in some university distribution systems. If that is what the utility is providing as a primary voltage, and if you want 208/120 for your building, then you need to get a transformer rated per your description.
Here is a paper I stumbled across where the first few pages discuss the evolution of distribution voltages:
http://www.cooperindustries.com/con...urces/library/201_1phTransformers/R201902.PDF
Here is a paper I stumbled across where the first few pages discuss the evolution of distribution voltages:
http://www.cooperindustries.com/con...urces/library/201_1phTransformers/R201902.PDF