The rules of 450.3B are for the protection of the transformer only. In general, the primary protection is set at 125% of the primary current. Due to the transformer inrush current or some other load on the transformer it may be necessary to increase this rating and the max setting is 250%.That said, my question is if you raise the OCPD using the percentages listed in Table 450.3(B) is it required (or even a good idea) to use a larger corresponding conductor ampacity rating as per 240.4?
DonThe primay conductors must be protected at or below their ampacity.
Just remember you can go by the 75degree column if all terminals in that circuit are rated at 75 degree or more even if it's under 100 amps. But if there is a 60 terminal in that circuit then you do have to us the 60 degree column.gary b said:I thought you used the 60 degree column (110.14(C)(1)(a) for 100 amps or less unless you check the listings for higher temps then you can use the 75 degree column.
That said, my question is if you raise the OCPD using the percentages listed in Table 450.3(B) is it required (or even a good idea) to use a larger corresponding conductor ampacity rating as per 240.4? I thought the tap rules in 240.21 (C) applied the secondary not the primary conductors.