We recently had invited by our vendor for the load testing of generator. The generator is 150kVA prime rated tested on load bank with unity power factor. The load test was going fine from no load to 100% load. We asked to test genset on 110% load i.e at 132kw. Since the generator is of prime rating it should withstand 110% load for one hour by the definition of prime rated generator set but, the generator get shut down due to temperature rise(107C) goes beyond temperature limit(96C).
The arrangement of generator was such that the load bank was placed near to the alternator side.
The technical team of the vendor give the justification for generator shutdown is due to hot air released by load bank sucked by alternator into the generator canopy causing temperature to rise beyond the threshold limit.
Is this the correct justification??
Is there any possibility of temperature rise due to unity power factor load bank??
Sent from my iPhone using Tapatalk
We recently had invited by our vendor for the load testing of generator. The generator is 150kVA prime rated tested on load bank with unity power factor. The load test was going fine from no load to 100% load. We asked to test genset on 110% load i.e at 132kw. Since the generator is of prime rating it should withstand 110% load for one hour by the definition of prime rated generator set but, the generator get shut down due to temperature rise(107C) goes beyond temperature limit(96C).
The arrangement of generator was such that the load bank was placed near to the alternator side.
The technical team of the vendor give the justification for generator shutdown is due to hot air released by load bank sucked by alternator into the generator canopy causing temperature to rise beyond the threshold limit.
Is this the correct justification??
Is there any possibility of temperature rise due to unity power factor load bank??
Sent from my iPhone using Tapatalk