I had a problem with a Pringle switch and I am going to pass on to you the solution.
When we had a very damp day with a lot of moisture in the air, sometimes a fuse would blow on one phase. This was a 600 volt, 3-phase 600-amp. switch.
I had the men check the load side wiring with a 1000 volt megger, but they could not find any bad readings to ground, or shorted across phases.
The first-line supervisor wanted to use a hypot tester to find the problem, but I would not allow him to use the hypot, my feeling is that the hypot can be a destructive test.
Well one day, when I was not available and a fuse blew, the first-line supervisor used the hypot tester on the Pringer switch load side wiring, and he found the problem. The switch was mounted on a slate material. When he applied a high voltage,(and I do not recall what voltage level that he applied) he found on the slate a track of current going to ground. And this was our problem. They dug out the burnt track in the slate, and sealed it with an insulating glyptal. They were able to put the switch back in service and then he ordered a new slate for the switch. Moral of this story, we would never have found the problem with using the megger. I am thinking now, if we had used the 5000 volt megger, would we have found the problem initially.