joeyww12000
Senior Member
- Location
- Chatsworth GA
After reading one of my several posts on grounding and bonding I noticed a design flaw in the prints on my current job. 3/0cu derived phase conductors on a seperately derived system, specs call for 1/0cu GEC. Thats fine just oversized, but system equipment bonding jumper calls for #6cu to be pulled with phase conductors to panel? Is this correct or doesnt the equipment bonding jumper need to be a 1/0cu also?