5.5.4 When classifying buildings, careful evaluation of prior experience with the same or similar installations should be made. It is not enough to identify only a potential source of the combustible material within the building and proceed immediately to defining the extent of either the Class I, Division 1 or Division 2; or Class I, Zone 1 or Zone 2 classified areas. Where experience indicates that a particular design concept is sound, a more hazardous classification for similar installations may not be justified. Furthermore, it is conceivable that an area be reclassified from either Class I, Division 1 to Class I Division 2, or from Class I, Division 2 to unclassified, or from Class I, Zone 1 to Class I, Zone 2, or from Class I, Zone 2 to unclassified, based on experience.