problem with power

Status
Not open for further replies.

mj324

Member
WE HAVE A 30 UNIT APARYMENT ONE OF THE UNITS IS FINE WITH NOTHING ON 120 BETWEEN NEUTRAL AND HOT GROUND AN HOT 217 ACROSS EACH LEG, WHEN WE TURN ANY BREAKER ON WE HAVE 120 ON NEATRUL AND 217 BTWEEN NEATRUL AND 1 PHASE THE OTHER PHASE DROPS TO ABOUT 45 VOLTS AND IT REVERSES DEPENDING ON WHICH PHASE YOUR ON
 
You have an open neutral.
Please turn your caps Lock off, we can hear you fine without yelling at us.

Roger
 
I agree with Roger, you have an open neutral somewhere and the voltage is dividing based on the load on each ungrounded conductor.
 