LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
Hey, gang. I got a job to look at a service in a large mall. Each store has sub-metering so the mall can recoup electrical costs from the stores. This service is a bottom-fed 480/277 at 2500a.
There are two sub-meters, one an E-mon D-mon and the other has a meter that is shaped like a POCO meter, in a plastic base. I can see both sets of CT's on the busbars through the perforated front panel.
The 2500a main breaker is about 2' up, and the CT's are 18" above it, where the busbars turn from vertical toward the cabinet's rear and then connect to the cabinet to the left, where the feeder breakers live.
Both meters show the present voltages, currents, KVA's and/or KW's, but neither one shows any accumulated KWH's. Is there anything that could happen that would cause both to do this?
The call originated as a troubleshoot, but I recommended removing both and installing a new E-mon D-mon kit rather than spend the time, and my proposal was accepted. The new kit is on order.
However, I am still very interested if anyone has an idea about why both meters would have the same symptoms. But, as Arlo Guthrie said, I didn't come here to tell you that story, but this one:
I'm posting this in Safety because what I really want to know is:
1. What should I have the store shut down before I touch anything? We'll probably do this on a Sunday evening for maximum time.
2. Do I merely shut off the main, or should I, as I think, shut off the sub-panel breakers first to minimize the load? Anything else?
3. Although I'll be a couple of feet above the incoming conductors below the main, can anyone recommend additional safety steps?
4. What about re-energization when I'm done? What have I forgotten to ask?
5. Most important, will I isolated enough to consider what I need to do not qualifying as working live? I want to be both safe and legal.
As always, Danke!
There are two sub-meters, one an E-mon D-mon and the other has a meter that is shaped like a POCO meter, in a plastic base. I can see both sets of CT's on the busbars through the perforated front panel.
The 2500a main breaker is about 2' up, and the CT's are 18" above it, where the busbars turn from vertical toward the cabinet's rear and then connect to the cabinet to the left, where the feeder breakers live.
Both meters show the present voltages, currents, KVA's and/or KW's, but neither one shows any accumulated KWH's. Is there anything that could happen that would cause both to do this?
The call originated as a troubleshoot, but I recommended removing both and installing a new E-mon D-mon kit rather than spend the time, and my proposal was accepted. The new kit is on order.
However, I am still very interested if anyone has an idea about why both meters would have the same symptoms. But, as Arlo Guthrie said, I didn't come here to tell you that story, but this one:
I'm posting this in Safety because what I really want to know is:
1. What should I have the store shut down before I touch anything? We'll probably do this on a Sunday evening for maximum time.
2. Do I merely shut off the main, or should I, as I think, shut off the sub-panel breakers first to minimize the load? Anything else?
3. Although I'll be a couple of feet above the incoming conductors below the main, can anyone recommend additional safety steps?
4. What about re-energization when I'm done? What have I forgotten to ask?
5. Most important, will I isolated enough to consider what I need to do not qualifying as working live? I want to be both safe and legal.
As always, Danke!