Ricko1980
Member
- Location
- San Francisco
- Occupation
- Electrical Contractor
I'm hunting around for a pull can that satisfies PG&E's green book requirements for a difficult service upgrade, and am curious if anyone has any models that have pleased the good folks at PG&E.
The new service is 400A one phase residential. PG&E wants 4" conduit from their vault.
The inspector wants us to propose a can for side entry, since the can will be in a basement area and we can just go straight in from 2' below sidewalk grade. Per the Green Book, I understand we need 42" inside the can between the closest edge of the incoming 4" conduit and the nearest termination bolt. This is a hugely giant can! Anyone have experience with this sort of PG&E situation, and found a product that works for them?
We're hoping to find a can with the termination bolts much closer to one end than the other, so we can get the 42" on the PG&E side, but keep the load side much shorter, since we have a space limit due to a stair. PG&E is only running 350 kcmil, so this can will look pretty much empty even once the wires are pulled....
Thanks for any thoughts!
Eric
The new service is 400A one phase residential. PG&E wants 4" conduit from their vault.
The inspector wants us to propose a can for side entry, since the can will be in a basement area and we can just go straight in from 2' below sidewalk grade. Per the Green Book, I understand we need 42" inside the can between the closest edge of the incoming 4" conduit and the nearest termination bolt. This is a hugely giant can! Anyone have experience with this sort of PG&E situation, and found a product that works for them?
We're hoping to find a can with the termination bolts much closer to one end than the other, so we can get the 42" on the PG&E side, but keep the load side much shorter, since we have a space limit due to a stair. PG&E is only running 350 kcmil, so this can will look pretty much empty even once the wires are pulled....
Thanks for any thoughts!
Eric