hello,
i have some questions on a school homework project i am working on. i have a 480 75hp 3 phase motor ,91 FLA on nameplate, and it's fed from a 208/120 3 phase panel. when i figure out what size 208/480 xfmr i need i come up with 75653va (480x91x1.732). in my homework packet i can only use 75 or 112.5 kva. so i feel i must go up to the 112.5 xfmr. i want to protect the primary only so do i size the overcurrent protection for the primary 450.3(B) by 125% of the FLC from nec 430.250(96)? i have heard conflicting ways to do this. some guys say wire and protect the xfmr to it's full capabilities,but our teacher wanted us to size things only for the load at this time,this motor above. i need to size the conductors for this feed also. thanks Randy
i have some questions on a school homework project i am working on. i have a 480 75hp 3 phase motor ,91 FLA on nameplate, and it's fed from a 208/120 3 phase panel. when i figure out what size 208/480 xfmr i need i come up with 75653va (480x91x1.732). in my homework packet i can only use 75 or 112.5 kva. so i feel i must go up to the 112.5 xfmr. i want to protect the primary only so do i size the overcurrent protection for the primary 450.3(B) by 125% of the FLC from nec 430.250(96)? i have heard conflicting ways to do this. some guys say wire and protect the xfmr to it's full capabilities,but our teacher wanted us to size things only for the load at this time,this motor above. i need to size the conductors for this feed also. thanks Randy