To All:
I am new here and hope I posted this in the right place.
Recently I was offered a promotion. One of the requirements was to take a test a competency test.
The test consisted of one question in two parts.
Here it is.
A 25kva transformer supplies a load of 12 kw at a power factor of .6 lagging. find the percentage of full load the transformer is carrying.
If additional unity power factor loads are to be served with the same transformer, how many kw may be added before the transformer is at full load.
Does anyone else think this is an unfair question. I was not able to complete the test. I only got the first part of 80 %, any additional help would be appreciated.
Thanks,
Tom