Ivette said:
Did I need to classify it as per NEC and NFPA Class I Division II Group D? There is a way to avoid this and rebuilt the fire system using gas detectors and carbon monoxide detectors directly connected to the main monoting system. I have three propaine boiler in this room.
NFPA 497 5.4.3 Open flames and hot surfaces associated with the operation
of certain equipment, such as boilers and fired heaters,
provide inherent thermal ignition sources. Electrical
classification is not appropriate in the immediate vicinity of
these facilities. However, it is prudent to avoid installing
electrical equipment that could be a primary ignition
source for potential leak sources in pumps, valves, and so
forth, or in waste product and fuel feed lines.