Propane Fill Tank Conduit

I have done a minimal amount of explosionproof stuff.

I need to run a 120ft 3/4" conduit to a disconnect on building from a hardware store propane fill tank (#10 thhn - 20a 120v circuit).
I am not sure I have this all correct per code.
Seems like all fittings within the 1st 10ft need to be explosionproof.

Will this work:

Pump system explosionproof box female to 3/4 rigid (do I need an explosionproof male/female fitting here?)
-3/4 rigid to explosionproof capped elbow
-capped elbow to 3/4 rigid to 3/4 seal within 18" (do I need explosionproof male/female or can I put the rigid right in the capped elbow & seal?)
- then go underground 2ft and 90 out of the C1D1 area (can I use female/female explosionproof couplers and a 3/4 rigid 90 here to get 10ft out and then transition to normal rigid couplers for 110ft under ground in a trench and 90 up to a seal below the disconnect on the side of the building?)

Thank you for your help. I'd rather not screw this up.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
First question: Is the design compliant with Section 500.4? That should define your boundaries.
 