Hey everyone -
I’ve got a unique situation and trying to make sure we do it correctly. My concern is how to properly seal and protect wires through a metal roof penetration on a solar install.
Penetrating a metal roof is no laughing matter (for me) and salty air/corrosion are also of concern here. Appreciate everyone’s insight in advance.
Background
Coastal area
Standing seam roof
Using S-5 Clamps so not a ton of clearance between roof and modules
Using Aztech Washer Co/dektite style flashing (low profile and recommended for metal roof penetration)
Single String from SE Optimizers + Ground
Example of conduit methods
Considered Option 1
- 1/2in EMT or SCH 40 PVC through the Flashing Glands with a 90+ degree turn above gland
Considered Option 2
- PV Wire Directly into the gland and into conduit sitting just at surface level of roof below the boot*
Considered Option 3
- liquid tite through gland (is ribbing going to make this a bad seal…?)
Actual flashing
Note: Penetration and flashing will be under a module.
Manufacturer shows PV wire going directly into the gland but have concerns about strain relief on the PV wire before the flashing gland and proper bushing/protection at penetration.
*Better option I have not considered?
I’ve got a unique situation and trying to make sure we do it correctly. My concern is how to properly seal and protect wires through a metal roof penetration on a solar install.
Penetrating a metal roof is no laughing matter (for me) and salty air/corrosion are also of concern here. Appreciate everyone’s insight in advance.
Background
Coastal area
Standing seam roof
Using S-5 Clamps so not a ton of clearance between roof and modules
Using Aztech Washer Co/dektite style flashing (low profile and recommended for metal roof penetration)
Single String from SE Optimizers + Ground
Example of conduit methods
Solar Multi-Port MR Master Flash® – Aztec Washer Company
masterflash.aztecwasher.com
Considered Option 1
- 1/2in EMT or SCH 40 PVC through the Flashing Glands with a 90+ degree turn above gland
Considered Option 2
- PV Wire Directly into the gland and into conduit sitting just at surface level of roof below the boot*
Considered Option 3
- liquid tite through gland (is ribbing going to make this a bad seal…?)
Actual flashing
Solar Multi-Port Square Base Flashing
ACCOMMODATES: one - 0" to 2" pipe two - 3/8" pipe/cable two - 3/4" pipe/cable DETAILS: allows for up to 4 cables or wires per flashing extra ports accommodate copper pipe & electrical cables easy installation for solar applications
protechonline.net
Note: Penetration and flashing will be under a module.
Manufacturer shows PV wire going directly into the gland but have concerns about strain relief on the PV wire before the flashing gland and proper bushing/protection at penetration.
*Better option I have not considered?