I have been having this discussion with quite a few people and I am getting mixed feed back. I am going to post my methods here and please tell me if I am wrong.
To properly size a generator you must know the load calculation of the house per NEC 220.
If you generator puts equal or more than your calculated figure your install meets 702.4
If your generator puts out less than figure you calculated you must install load shedding as per NEC 702.4
...........................................................
This scenario is set up using a 200A whole home ATS and a 20kw generator.
The load was calculated as per NEC 220 with this excel work sheet www.piertopier.us/hvac/RCO_Automated_Rev2.xls
The CalSheet calls for 152.21A
The home currently has A 200A service.
The customer ordered a 20kw Generator and 200A Service Entrance ATS
In order for this installation to be code compliant you must install load management.
...........................................................
Thanks
Sam
To properly size a generator you must know the load calculation of the house per NEC 220.
If you generator puts equal or more than your calculated figure your install meets 702.4
If your generator puts out less than figure you calculated you must install load shedding as per NEC 702.4
...........................................................
This scenario is set up using a 200A whole home ATS and a 20kw generator.
The load was calculated as per NEC 220 with this excel work sheet www.piertopier.us/hvac/RCO_Automated_Rev2.xls
The CalSheet calls for 152.21A
The home currently has A 200A service.
The customer ordered a 20kw Generator and 200A Service Entrance ATS
In order for this installation to be code compliant you must install load management.
...........................................................
Thanks
Sam