Re: Proper Grounding for Pool Lift
You should have an engineer familiar with the NEC write your instructions. I'll give you this much:
You need to distinguish between equipment grounding and the pool bonding grid. If this lift is metal or mounts to metal sockets in/on a pool deck, then all of that metal must be connected to the pool bonding grid (which is a series of #8 solid copper wires in/under the concrete and also exteneded to the pool rebar, pump, underwater lights, metal handrails, and perhaps a bunch of other stuff).
All of the metal parts on your lift must be electrically well bonded together (structure, enclosures, motors, etc). If they are not, you'll need to provide lugs where #8 solid wire can be field installed to interconnect any the isolated metal parts. I would hope you take care of that issue at the factory...
The electric equipment on this lift must be grounded with an equipment grounding wire in the branch circuit(s) feeding this lift. I can't tell you what size or if it needs to be green insulated. Have someone read NEC 625 and NEC 250.122 to figure that out. This equipment grounding conductor will attach to some place metal that is already bonded to the #8 bonding grid. So there is sort of a double system for grounding/bonding, which is intentional.