The power company doesn't allow grounding in the meter pans.
The service I am installing:
2" mast with 4/0 Al SECs
2 gang meter pan
2 individual nipples run inside to 2 100A main breaker panels
water pipe and 2 ground rods will be used for electrodes
How do I ground/bond these 2 panels?
What I plan on doing is running the #4 from the water pipe and the #6 from the ground rods into 1 panel, then running a #4 jumper from that panel to the other panel. That should be compliant, correct?
Also, I could run #2 AL from each meter to each 100A panel since it's carrying the load of the entire apartment, correct?