wmeek

Senior Member
Location
Texas
Occupation
Electrician
This is my scenerio: I have a 320 Meter can and i am running parallel 2" emt from meter can up to the bottom of a
6x6 Gutter. Also to the left of these 2" conduits will be a 1phase 200A disconnect and a 3phase 200 amp disconnect hanging from the bottom of gutter. 1phase disconnect will have 2-3/0 , 1-2/0 , and 3phase disconnect will have 3-3/0, 1-3/0. Also in the gutter will be a 1/0GEC Bldg. steel, 1/0 Gec to water pipe and #4 to each disconnect. 1-#4 to all bonding bushings in gutter. GEC to ground rod will be ran to meter can(per Utility).6(A). I came up with a 6x6 gutter size per 366.22 and 312-6(a).My question is this code compliant installation.
 
If you have 2" pipe going in the bottom and 2" going down to the disconnect then you have a Upull. 314.28(A)(2). The gutter should be sized 6 x 2" -- 12" high.