J juancarlos2003 Member Mar 29, 2004 #1 Dear sirs. THHN/THHW insulation is adequate for underground duct bank installation? Which are the limitations for use?
Dear sirs. THHN/THHW insulation is adequate for underground duct bank installation? Which are the limitations for use?
ryan_618 Senior Member Location Salt Lake City, Utah Mar 29, 2004 #2 Re: Proper insulation selection Anything underground is considered to be a wet location, and therefore a "w" must be on teh insulation of the conductor.
Re: Proper insulation selection Anything underground is considered to be a wet location, and therefore a "w" must be on teh insulation of the conductor.
charlie Senior Member Location Indianapolis Mar 29, 2004 #3 Re: Proper insulation selection Juan, please don't address us as sirs, the ladies may be offended. Take a look at 310.13 for more information about your question.
Re: Proper insulation selection Juan, please don't address us as sirs, the ladies may be offended. Take a look at 310.13 for more information about your question.
J jschultz Member Mar 30, 2004 #4 Re: Proper insulation selection thwn is not rated for 90 degrees. So remember that when derating.