So to make a long story short, according to the article, the 25A breaker is a recommended size, and not a maximum size. The breaker could be sized anywhere up to 49 amps.
Confusing, because of the way the 25 is listed below the "Max Fuse Size", most people assume its also a max breaker size.
Also, according to the article, the NEC doesn't require the breaker size to be larger than the MCA. That's different than what I always believed - I thought the branch circuit size had to be as large as the MCA, and I thought that included the breaker size.
That explains a lot, because we have seen at least a few other similar posts.