Proper Method to Reset a tripped Circuit Breaker

Status
Not open for further replies.

PCBelarge

Member
Location
Westchester County NY
Occupation
Electrical Training and Consulting
I am in the process of setting up a class for troubleshooting tripped circuit breakers procedure.
Do you guys have any procedures that may or may not be exactly by "the book?"
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
You may want to look into what OSHA has to say about that subject.
Since your teaching a class OSHA info should be included.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Yes as said in post 2, unless you are sure that the trip was caused by an overload, you are not permitted to reset it without investigating the reason for the trip.
 

PCBelarge

Member
Location
Westchester County NY
Occupation
Electrical Training and Consulting
Thanks for the replies. I have downloaded Manufacturers' procedures, NETA procedures an other information.
I was hoping for some "in field" experiences.
As you all know there is some terrible information to be had online and very few have been taught the proper means.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Here is how not to do it. My coworker went to reset a circuit breaker at a parking garage, where the panel was embedded in a concrete wall with an overhead service drop water had gotten into the panel from the service drop in the breaker tripped he reset the breaker and and there was a large arc flash, but he was not hurt. I would’ve remove the cover from the panel and inspected it first. When I breaker trips, there is normally a reason often it’s just an overheating connection on the load side of the breaker creating heat.
Hello Pierre.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Here is how not to do it. My coworker went to reset a circuit breaker at a parking garage, where the panel was embedded in a concrete wall with an overhead service drop water had gotten into the panel from the service drop in the breaker tripped he reset the breaker and and there was a large arc flash, but he was not hurt. I would’ve remove the cover from the panel and inspected it first. When I breaker trips, there is normally a reason often it’s just an overheating connection on the load side of the breaker creating heat.
Hello Pierre.
That’s basically what OSHA says, do not reset the breaker until the problem is found. Definitely good advice for larger breakers. Should be done for small breakers too, but most electricians will reset them hoping it was just an overload. (Guilty as charged, LOL!) usually you will know instantly wether it was an overload, or a short circuit. Resetting frequently will damage the breaker and possibly cause an arc flash or even worse.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Let your class know if you reset a 20 A and it trips immediatly then thats a dead short. And hard on the breaker!
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If I may recommend a method for short circuit troubleshooting a short:

When troubleshooting a circuit with a direct short circuit to either neutral or ground, it's difficult to find the fault because you can't keep the power on, so the only way to find the offending undesired connection is visually, box by box.

I typically use a rubber socket with a 150-watt bulb screwed into it, and wire it in series with the problem circuit at the panel. I disconnect the circuit's hot wire from the breaker terminal, connect the socket's black wire to the breaker, and wire-nut the circuit's hot wire to the socket's white wire.
leviton-lamp-accessories-124-d-a0_1000.jpg
With the high-wattage bulb in series with the circuit, the breaker will stay on because the most current that can flow is that of the bulb, so it acts as a current limiter. It also functions as an indicator, steady bright for a direct short, flickering for an arcing fault, etc., with you or a helper watching it.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
This is obvious to most, but the breaker must be turned all the way off, then back on. I can't tell you how many times I've talked to someone (phone or in person) that says they have flipped the breaker several times and it won't reset. I explain (more than once) how to reset it but they insist it won't reset. I get there, flip it off, then back on and it resets. "What did you do?" asks the customer. I said I did just what I told you several times to do!

***Note, I do tell them that if it sets then "pops" right back off, to leave it alone until it can be checked.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
This is obvious to most, but the breaker must be turned all the way off, then back on. I can't tell you how many times I've talked to someone (phone or in person) that says they have flipped the breaker several times and it won't reset. I explain (more than once) how to reset it but they insist it won't reset. I get there, flip it off, then back on and it resets. "What did you do?" asks the customer. I said I did just what I told you several times to do!

***Note, I do tell them that if it sets then "pops" right back off, to leave it alone until it can be checked.
Been there a number of times as well.:rolleyes::ROFLMAO:
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I've had people tell me to look away. I knew one guy who would reset large breakers with a broom handle while standing to the side. I honestly don't know what OSHA says.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Electrical myths:
1) If the breaker keeps tripling ... just keep resetting it. It will eventually clear itself !
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
Say three Hail Marys , Turn your face away from the panel, Take a deep breath and hold it, Then let'er rip
 

David Castor

Senior Member
Location
Washington, USA
Occupation
Electrical Engineer
To close a breaker, stand to the side and turn your head. Use the hand that allows the greatest distance from the panel. For 480 V breakers, we recommend PPE be worn, especially eye and face protection.
 
Status
Not open for further replies.
Top