underground meter socket,
e.m.t. to meter socket
bonding bushing in meter socket with wire to grounded conductor bar which is bonded to socket,
inside load center bonding bushing on e.m.t. with
wire to grounded conductor bar which is bonded to load center.Grounding electrode from water system and ground rods to grounded conductor bar.
Code states standard locknuts cannot be used on line side of service so bonding bushings must be used because of knockouts in equipment. Meter socket comes from factory with grounded conductor bar bonded to it and is listed as such.
Code states grounded conductor is to be bonded at
service disconnect. Any thoughts????????
e.m.t. to meter socket
bonding bushing in meter socket with wire to grounded conductor bar which is bonded to socket,
inside load center bonding bushing on e.m.t. with
wire to grounded conductor bar which is bonded to load center.Grounding electrode from water system and ground rods to grounded conductor bar.
Code states standard locknuts cannot be used on line side of service so bonding bushings must be used because of knockouts in equipment. Meter socket comes from factory with grounded conductor bar bonded to it and is listed as such.
Code states grounded conductor is to be bonded at
service disconnect. Any thoughts????????