I'm being tasked with designing and installing the branchcircuit wiring for the following scenario:
I am installing 4power distribution units (PDU) (which is IT lingo for fancy power strips) ratedat 30 amps each in a data server room. The total load being served currently is 19600watts but I want to size everything for the full 30 amps and I'm going to divide this up between the 4 PDU units on 4 separate circuits.I'm going to supply this load with 208 volts from a 120/208 volt 3-phase panel.Which calculates to 23.6 amps per PDU.
My confusion isthis: These PDU units come with a NEMA 30amp plug to go into a standard 30 ampNEMA receptacle. The code is clear that I have to upsize both my conductor andbreaker 125% because it’s a continuous load and because its IT equipment645.5(A)….which I interpret as meaning conductor capable of 37.5amps (8 gauge)and a breaker rated at 40 amps….but the code also states at 210.21 (B) (1) thata single receptacle on an individual branch circuit cannot have an amp ratingless than the circuit. In addition Table 210.21 (B)(3) seems to back this upthat a 30 amp receptacle must be installed on a 30 amp circuit.
How can I upsize125%? And still meet the requirements of 210.21 (B)(1)
I'm sure this is a probably a dumb question andan easy answer and I'm just not grasping the whole concept, but if you couldset me straight I would sure appreciate it!!
I am installing 4power distribution units (PDU) (which is IT lingo for fancy power strips) ratedat 30 amps each in a data server room. The total load being served currently is 19600watts but I want to size everything for the full 30 amps and I'm going to divide this up between the 4 PDU units on 4 separate circuits.I'm going to supply this load with 208 volts from a 120/208 volt 3-phase panel.Which calculates to 23.6 amps per PDU.
My confusion isthis: These PDU units come with a NEMA 30amp plug to go into a standard 30 ampNEMA receptacle. The code is clear that I have to upsize both my conductor andbreaker 125% because it’s a continuous load and because its IT equipment645.5(A)….which I interpret as meaning conductor capable of 37.5amps (8 gauge)and a breaker rated at 40 amps….but the code also states at 210.21 (B) (1) thata single receptacle on an individual branch circuit cannot have an amp ratingless than the circuit. In addition Table 210.21 (B)(3) seems to back this upthat a 30 amp receptacle must be installed on a 30 amp circuit.
How can I upsize125%? And still meet the requirements of 210.21 (B)(1)
I'm sure this is a probably a dumb question andan easy answer and I'm just not grasping the whole concept, but if you couldset me straight I would sure appreciate it!!