proper use of amp meters for a novice

Status
Not open for further replies.

kspifldorf

Senior Member
Im trying to come up with a procedure for proper use of an amp meter for training discussion for our maintenance guys Im afraid that im being too general need some specific ideas Thanks KEG
 

cpal

Senior Member
Location
MA
What type of Ammeter ?? clamp on ?? Hard Wired?? Digital , analog?????

Turn off power pri to insertion in circuit
Start at highest scale
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
If the meter is going to be used on an energized circuit you should follow NFPA 70E. If you are chosing PPE under the task tables of NFPA 70 table 130.7(C)(9)(a) a double layer switching hood must be worn (see note 2*).
 

sparky_magoo

Senior Member
Location
Reno
jim dungar said:
If the meter is going to be used on an energized circuit you should follow NFPA 70E. If you are chosing PPE under the task tables of NFPA 70 table 130.7(C)(9)(a) a double layer switching hood must be worn (see note 2*).

Does this mean I should stop sticking my clamp meter into energized panelboards?
 

tallgirl

Senior Member
Location
Great White North
Occupation
Controls Systems firmware engineer
sparky_magoo said:
Does this mean I should stop sticking my clamp meter into energized panelboards?

Just be sure to turn off the panelboard first. :D

I like to leave mine out in the rain. Which probably explains why it doesn't work ...
 